    Ok so I got this little dilemma at work. For a small job we had to run 3/8 poly tube from one end of a building to another. We use regular PVC electrical conduit as a sheath for the 3/8 poly tubing. Now I'm being told by a supervisor that we cannot use the electrical conduit as a shoot for the poly tube and he's telling us that you can only run electrical cables through electrical conduit.
    My question is is this true we can't find any code that says you can only run electrical cables through electrical conduit does anybody have any knowledge on this.

    0 Not allowed! Not allowed!
    2016 triumph street triple R
    "A Journey must begin with one step"

  2. #2
    Lifer Falko's Avatar
    Join Date
    Mar 2010
    Location
    MoonTown
    Posts
    5,104

    Re: Electrical conduit help

    I've seen pneumatic control tube run through conduit in dangerous locations. It was vented though so no pressure could build within the conduit causing it to burst.

    I could see there being an issue if the tubing you are running carries a flammable gas where a leak would allow build up and possible explosion.

    I've never seen a code saying you couldn't do what you are doing.

    0 Not allowed! Not allowed!
    Dad's Dream: Earn enough money to live the life that his wife and kids do.

  3. #3
    Member Johnpewpew's Avatar
    Join Date
    Aug 2017
    Location
    Chicopee, MA
    Posts
    240

    Re: Electrical conduit help

    Yeah I actually think I just found my answer. On the Conduit itself it doesn't actually say it's electrical conduit it just says it's plain old conduit which by definition could be used for anything.

    0 Not allowed! Not allowed!
    2016 triumph street triple R
    "A Journey must begin with one step"

  4. #4
    Lifer loudbeard's Avatar
    Join Date
    Jun 2013
    Location
    Rehoboth MA
    Age
    37
    Posts
    4,437

    Re: Electrical conduit help

    If you're installing something in electrical conduit, it should be electrical. That is it's intended purpose, the reason it isn't in the code is the code applies to electrical devices, which poly tube is not. "Please don't install air and liquid lines in raceways" should be a no brainer. Your boss is right.

    As Falko said, sometimes people use conduit as a protective sleeve when you near ground level or potential pinch points. There are provisions in the code which allow for atypical installation under "engineering supervision," this is intended for industrial applications where the code is either insufficient or too binary to cover the application. PVC electrical conduit is not intended to be a pressure vessle; the couplings aren't rated for it and the glue isn't rated for it. If you are going to use it as a sleeve, it needs to be vented. Regarding the conduit "not actually saying it's electrical" if the pipe looks like below...it's electrical:
    Electrical conduit help-electrical-jpg

    1 Not allowed! Not allowed!
    I went to MMI I know what Im doing here chief

  5. #5
    Lifer Falko's Avatar
    Join Date
    Mar 2010
    Location
    MoonTown
    Posts
    5,104

    Re: Electrical conduit help

    Electrical conduit, it's a "grey" area...

    2 Not allowed! Not allowed!
    Dad's Dream: Earn enough money to live the life that his wife and kids do.

  6. #6
    Member Johnpewpew's Avatar
    Join Date
    Aug 2017
    Location
    Chicopee, MA
    Posts
    240

    Re: Electrical conduit help

    Ok so There is no code that says we cant use this to protect are tubing. Just fround apon as industy practice. But its a big gray area.

    Just a little more info on this job. There are no wiers in this line or near just the 3/8 tubing. It is open on both ends. We used this conduit for its long sweep 90's.

    0 Not allowed! Not allowed!
    2016 triumph street triple R
    "A Journey must begin with one step"

  7. #7
    Lifer loudbeard's Avatar
    Join Date
    Jun 2013
    Location
    Rehoboth MA
    Age
    37
    Posts
    4,437

    Re: Electrical conduit help

    I donít know much about plumbing code, which is what would apply here.


    Sent from my iPhone using Tapatalk

    0 Not allowed! Not allowed!
    I went to MMI I know what Im doing here chief

  8. #8
    Member Johnpewpew's Avatar
    Join Date
    Aug 2017
    Location
    Chicopee, MA
    Posts
    240

    Re: Electrical conduit help

    Ya he could be right. I'm not saying he's wrong but he is a colossal douchebag. So I assume he is wrong.

    0 Not allowed! Not allowed!
    2016 triumph street triple R
    "A Journey must begin with one step"

  9. #9
    ....................... PinHead's Avatar
    Join Date
    Jun 2001
    Location
    Walpole
    Age
    51
    Posts
    5,157

    Re: Electrical conduit help

    Is there any pressure in this line? Flammable liquid? If it is just for protection so the flexible tubing is protected against bumps and such I don't think there is any code to stop you from doing it. Plumbing tubing would be more appropriate, but you are not breaking any codes I don't think. You are not technically using it for electrical so our codes wont apply. I bent up and painted some 3/4 emt and use them to hold bird feeders in my back yard, is that against code? Nope!

    2 Not allowed! Not allowed!
    2018 Harley Road Glide
    2000 Ducati 900ss
    2018 Onewheel XR

  10. #10
    Member Johnpewpew's Avatar
    Join Date
    Aug 2017
    Location
    Chicopee, MA
    Posts
    240

    Re: Electrical conduit help

    Ya we argued the hell out of it with him and got him to admit he just didint like how it looked.

    0 Not allowed! Not allowed!
    2016 triumph street triple R
    "A Journey must begin with one step"

  11. #11
    ain't nuttin wrong w/that scubasteveRR's Avatar
    Join Date
    May 2009
    Location
    Cambridge, ma
    Age
    42
    Posts
    3,278

    Re: Electrical conduit help

    so whats the verdict... you have to do it all over again?

    0 Not allowed! Not allowed!

  12. #12
    Member Johnpewpew's Avatar
    Join Date
    Aug 2017
    Location
    Chicopee, MA
    Posts
    240

    Re: Electrical conduit help

    Quote Originally Posted by scubasteveRR View Post
    so whats the verdict... you have to do it all over again?
    Oh ya it all came back down lol.

    0 Not allowed! Not allowed!
    2016 triumph street triple R
    "A Journey must begin with one step"

  13. #13
    Lifer Stromper's Avatar
    Join Date
    Mar 2010
    Location
    Eastern Ct
    Posts
    3,249

    Re: Electrical conduit help

    I do not agree with your boss, it is just acting as armor not carrying anything
    Some believe only iron is good for air which is also nuts

    He's the boss though so by definition he is right as long as you have the time and materials to do it his way

    Steel conduit would not droop though

    I ran an entire 40,000 square feet with grey PVC air, water, and coolant emulsion no problem, also made it super simple to add a drop

    0 Not allowed! Not allowed!
    Last edited by Stromper; 11-03-17 at 04:13 PM.
    The calculus of hate

    It is not that I should win it is that you should lose
    It is not that I succeed it is that you fail
    It is not that I should live it is that you should die

  14. #14
    Member Johnpewpew's Avatar
    Join Date
    Aug 2017
    Location
    Chicopee, MA
    Posts
    240

    Re: Electrical conduit help

    Yeah I work for a municipality. So I got time to do it twice. I'll just to spite him we might do it a third time.

    0 Not allowed! Not allowed!
    2016 triumph street triple R
    "A Journey must begin with one step"

  15. #15
    Lifer Jayspeed's Avatar
    Join Date
    Apr 2007
    Location
    Medford, MA.
    Age
    42
    Posts
    1,169

    Re: Electrical conduit help

    If the manufacturer of said conduit list's and labels it's conduit to do other than electrical like pneumatic. Then ya its ok. Never seen pneumatic in conduit but then I'm not looking out for that. Is that what you are running? Isn't the tubing you run rated to be run on its own?

    0 Not allowed! Not allowed!
    Jay
    2013 gixxer 750
    2009 Ducati M1100s
    2017 KTM exc-f 350

  16. #16
    Member Johnpewpew's Avatar
    Join Date
    Aug 2017
    Location
    Chicopee, MA
    Posts
    240

    Re: Electrical conduit help

    Quote Originally Posted by Jayspeed View Post
    If the manufacturer of said conduit list's and labels it's conduit to do other than electrical like pneumatic. Then ya its ok. Never seen pneumatic in conduit but then I'm not looking out for that. Is that what you are running? Isn't the tubing you run rated to be run on its own?
    It's not an pneumatic line it's going to be for a chemical feed. The liner running will be 12 feet in the air away from bumps scratches and Machinery the tubing can perfectly be by itself but again supervisor says do it I do it.

    0 Not allowed! Not allowed!
    2016 triumph street triple R
    "A Journey must begin with one step"

  17. #17
    Lifer Jayspeed's Avatar
    Join Date
    Apr 2007
    Location
    Medford, MA.
    Age
    42
    Posts
    1,169

    Re: Electrical conduit help

    Quote Originally Posted by Johnpewpew View Post
    It's not an pneumatic line it's going to be for a chemical feed. The liner running will be 12 feet in the air away from bumps scratches and Machinery the tubing can perfectly be by itself but again supervisor says do it I do it.
    So its a chemical fluid line run through electrical tubing? I don't see any danger in it. Authority having jurisdiction will have a final call on it. I don't see anything wrong with physical protecting something with a conduit sleeve. Maybe a label on the conduit of its contents? Only thing to consider is the trade of the practice and what it's requirements are. Does this fall under plumbing for example? Probably not. But it may be the better path to take since it is a fluid.

    0 Not allowed! Not allowed!
    Last edited by Jayspeed; 11-03-17 at 06:55 PM.
    Jay
    2013 gixxer 750
    2009 Ducati M1100s
    2017 KTM exc-f 350

  18. #18
    Member Johnpewpew's Avatar
    Join Date
    Aug 2017
    Location
    Chicopee, MA
    Posts
    240

    Re: Electrical conduit help

    Ya idk what the hell this guy is thinking. And to top it all off this is all temp. It's for a trial. It's for an Odor Control solution at one of our pump stations. It will most likely be gone within the year anyways.

    0 Not allowed! Not allowed!
    2016 triumph street triple R
    "A Journey must begin with one step"

  19. #19
    ain't nuttin wrong w/that scubasteveRR's Avatar
    Join Date
    May 2009
    Location
    Cambridge, ma
    Age
    42
    Posts
    3,278

    Re: Electrical conduit help

    sounds like a waste of money to me. Is this guys the "BOSS" boss. or is there someone higher. Maybe mention you think it's a waste of money.

    or just do it again and get paid twice, things are always easier the second time around?

    0 Not allowed! Not allowed!

  20. #20
    Lifer Jayspeed's Avatar
    Join Date
    Apr 2007
    Location
    Medford, MA.
    Age
    42
    Posts
    1,169

    Re: Electrical conduit help

    For temporary I wouldn't worry about it. This reminds me of a bar I was in a few months ago in Boston near Fenway. It had an open ceiling and there were several 4" EMT conduits run overhead and dropped down in the bar area. They had a lot of beer on tap. I think these sleeved and concealed the beer lines from kegs to taps. Edit: The Yard House. Thats the place. If thats the case, learn something new everyday. Edit: 2nd edit here but if you look at pictures of the bar and the conduit, that isn't EMT or rigid conduit. I don't know what that is.

    0 Not allowed! Not allowed!
    Last edited by Jayspeed; 11-04-17 at 04:32 PM.
    Jay
    2013 gixxer 750
    2009 Ducati M1100s
    2017 KTM exc-f 350

  21. #21
    Member Johnpewpew's Avatar
    Join Date
    Aug 2017
    Location
    Chicopee, MA
    Posts
    240

    Re: Electrical conduit help

    Quote Originally Posted by scubasteveRR View Post
    sounds like a waste of money to me. Is this guys the "BOSS" boss. or is there someone higher. Maybe mention you think it's a waste of money.

    or just do it again and get paid twice, things are always easier the second time around?
    It's defiantly a big East of time and money. But hey he's gotta justify his job some how lol. And it won't be easier the second time around will make damn sure of that