Results 1 to 18 of 18
Grounding my generator
    Apr 2004
    Wilmington, MA
    So I has a transfer panel put in my house 3 years ago by a licensed electrician but have never had to use it.
    Tonight prepping the generator I came across the wording that the generator need to be grounded for use.
    I vaguely remember the asking the electrician if I needed to ground the generator while In use of the transfer panel and I vaguely remember a “no”
    Is there a way I can simply confirm this ?
    I’m not a an electrical guy and well I could always just use some wire and a spike to be sure but I’d rather not drive down to Lowe’s if not needed
    Any insight if I need to ground or the transfer panel by default negates the need ?
    hmmmm......
    Lifer Gixxer's Avatar
    Sandown, NH
    Re: Grounding my generator
    Does the cable connecting your generator to your panel have a ground? If so, I would imagine it is grounded through the grounding system of your home. You would have to take the dead front off in your panel to be sure.
    Sandown, NH
    The twist lock should have a ground.
    Walpole
    There should be a ground lug on the frame of the gen., you should use a #8 solid copper wire to ground it. You can put an 8' ground rod into the ground near where you want to put the gen. when you are using it, that should cover the ground requirement. On the ground rod side they make what we call an "acorn clamp" that you would use to connect the wire to it.
    2018 Harley Road Glide
    2000 Ducati 900ss
    2018 Onewheel XR
    Sandown, NH
    Might be hard to drive an 8' rod in these conditions. A 45 degree angle is permitted, right? Isn't this supplemental grounding protection? Is the cable to the panel not enough?
    And the full 8' and acorn need to be buried.
    Walpole
    By code you don't need one because it is a "portable" generator. A ground rod will only help "bond" it to ground in case something happens.
    250.34 Portable and Vehicle-Mounted Generators.
    (A) Portable Generators. The frame of a portable generator
    shall not be required to be connected to a grounding
    electrode as defined in 250.52 for a system supplied by the
    generator under the following conditions:
    (1) The generator supplies only equipment mounted on the
    generator, cord-and-plug-connected equipment through
    receptacles mounted on the generator. or both, and
    (2) The normally non-carrying metal parts of equipment
    and the equipment grounding conductor terminals of
    the receptacles are connected to the generator frame.
    (B) Vehicle-Mounted Generators. The frame of a vehicle
    shall not be required to be connected to a grounding electrode
    as defined in 250.52 for a system supplied by a generator
    located on this vehicle under the following conditions:
    (1) The frame of the generator is bonded to the vehicle
    frame, and
    (2) The generator supplies only equipment located on the
    vehicle or cord-and-plug-connected equipment through
    receptacles mounted on the vehicle, or both equipment
    located on the vehicle and cord-and-plug-connected
    equipment through receptacles mounted on the vehicle
    or on the generator, and
    3) The normally non-current-carrying metal parts of equipment
    2000 Ducati 900ss
    2018 Onewheel XR
    Apr 2004
    Wilmington, MA
    8 feet ?!?!?! Wow. I don’t think u could do that even in summer maybe 5 in this soil and shale we have here
    Apr 2004
    Wilmington, MA
    Can’t seem to load a pic thru the phone. But it’s a reliant transfer panel. No twist lock cable just plug for panel and genny. 4 prongs on the cable.
    4 prongs have a ground.
    -Clayton
    2006 Suzuki SV650
    2004 Suzuki Vstrom 650
    Apr 2004
    Wilmington, MA
    And with that answer. I can go to sleep without worrying tonight. Thx
    Might be hard to drive an 8' rod in these conditions..
    I drill pilot holes thru the frost with an impact drill to set 5/8 rebar for property corners, drilling thru frost is generally a lot easier than drilling thru concrete or granite, so a cordless, or even corded, it's not like you're doing it a mile in the woods like me, I have an obsolete Ryobi 2stroke gas powered impact drill, uses SDS bits, I even use a larger 3/4" bit to make a pilot hole for wood grade stakes.
    Lifer Stromper's Avatar
    Eastern Ct
    First the neutral white wire and the ground are the same thing for 120V in your main box
    2nd DONT WORRY BE HAPPy
    or
    Worry you have enough fuel
    The calculus of hate
    Seacoast NH
    Dear lord!
    Nobody ever listen to this guy. Ever.
    Eastern Ct
    Take the cover off your breaker box and look where the whites are connected.... then publish an apology
    Seacoast NH
    You'll get no apology from me.
    Ground and neutral are BONDED in the primary load center in a home. That does not by any whackjob definition of the word equate to "are the same thing". You should never bond ground and neutral in multiple places. It should be bonded in exactly one place in a given system. If you have sub-panels they should be grounded through the main one. Your generator should be grounded through its various sub-panels to the primary as well.
    Your advice is at the very least a great way to introduce a grounding loop. Possibly worse.
    5 Not allowed! Not allowed!
    Before you start stabbing each other with frozen fish and for the other people like me who don’t know Dick about household electrical (but have a backup generator).
    The Neutral and Ground are generally connected together at your service panel, not at your devices.
    At the device, neutral is the path for return current. All the current that comes "from" the hot leg "returns" through the neutral wire. I'm using quote marks because current actually alternates directions in an AC system. Hence the name AC!
    Anyway, the ground wire should only carry current in the case of a fault condition. In the USA, residential ground wires are often just bare, uncovered copper. When plugging in a grounded appliance or other device, the ground wire gets attached to the chassis.
    Say, for example, that the insulation on your hot wire gets damaged and the conductor comes into contact with the metal body of your washing machine. The current shorts through the chassis and then through the ground wire. This high current causes your circuit breaker (or fuse) to trip. If you didn't have the ground wire then the mains voltage would electrify the entire chassis. Then the next person touching it becomes the return path
    “When it comes to the kitchen, I have a narrow band of competency.”
    Master Mechanic Roger Barr in “Chasing Classic Cars.”
    Lifer loudbeard's Avatar
    Idiot electrician who wired our facility decided to bond a 200 amp 208v 3 phase sub panel. It took a while but it melted the backplane of the breaker panel along with a few breakers. I’ll try and find that picture. Keep fighting the good fight Bubs.
    Eastern Ct
    The service big wire is in the buss bar
    The naked grounds are in the buss bar
    The white insulated wires are in the Buss Bar
    The Ground Stake is in the Buss Bar
    I was in a small plane once that did a ground loop